I can?t conceive in my mind why anyone would bond hot to cold.
Because the NEC does not say just bond what 'you' think will suffice it says bond the "system".
250.104 Bonding of Piping Systems and Exposed Structural
Steel.
(A) Metal Water Piping. The metal water piping system
shall be bonded
Now I agree that we need a sizing chart for bonding of trade sizes. 1/2", 3/4", etc.
If I had a plumbing leak and replaced my cold water line to the hot water tank with Pex but left the whole hot side in copper would you say do not worry about the hot water lines?