I work in jurisdictions that require demonstrating torque on every job, or at least a video of connectors being torqued with a tool.
But there's been a big problem with old aluminum feeder wires in apartments.
When torqued to the NSI/Polaris specifications, the bolts simply tear the aluminum conductors.

For example at 180 in/pounds for 1/0 AWG stranded aluminum.
This has been a problem when the AHJ insists on seeing a live demonstration of torque on the connector, and it tears.
You don't get too many chances on this, as these wires come out of the wall without a whole lot of slack.
Split bolts like the APS06 have similarly difficult to achieve torque values, but the design of a split bolt does not dig at the old cable quite as much.
Anyone deal with this situation and found a solution?