The point mentioned in serial no.2 of the said reference does not specifically state that it is applicable to indoor transformer only. So please don't mislead.
You have not provided a good link. Information gained from available snippets shows the heading to be:
Subject:- Provision of Transformer Substation & Engine Alternator in Telecom Buildings - ISSUE of Guidelines.
There is no misleading on my part, just trying to piece together the garbled mess you throw out.
Since we have addressed harmonics mitigation using k-factor transformers, what other adverse environmental conditions are you considering?
If the 85% is for a 1.18 factor-k for harmonics (about equivalent to a k-factor of 9), BSNL should be using k-factor transformers instead of de-rating standard transformers. Maybe inefficient decisions like that is why they have been bleeding money for years and are considered a sinking ship in the telecom sector.