Grounding electrodes only work as a shock control device by raising the voltage of the earth around the grounding electrode to that of the bonding conductor. If you are more than 5' from the rod, they have almost no effect on reducing the shock hazard.the earth rods are there to direct any surface or under surface voltage into the ground. large joules that travel across the surface and into the bonding (w/o rods) may/can wreak havoc on the items connected to the bonding. the rods only help to divert the joules into the ground.
equipotential bonding vs bonded to gnd (w/ earth rods), thats how i see it, and i like the latter better.
The pool bonding is intended to keep everything at the pool at the same potential. This will often be a potential that is above "earth" and that is why, in addition to the water and all of the pool equipment, the code requires the perimeter surface around the pool to also be bonded.