Pool bonding

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
Came across this yesterday . The Equipotential bonding wire that circles the pool was attached to a ground rod and the pool pump and water filter were attached also to ground rod. Any thoughts on this ?
 
Seemingly the waste of a ground rod but can't see where it is not allowed.
 
Seemingly the waste of a ground rod but can't see where it is not allowed.

If there is a panel out by the equipment then using the ground rod is unnecessary but it doesn't hurt, afaik... Eventually all the equipotential bonding does go back to the grounding electrodes anyway
 
Thanks, I didn't think the bonding was to go to a ground rod.
250.52 prohibits the pool bonding listed in 680.26 to be used as a facility grounding electrode but, as Dennis states, there is nothing prohibiting a ground rod in the 680.26 bonding.
 