Seemingly the waste of a ground rod but can't see where it is not allowed.
250.52 prohibits the pool bonding listed in 680.26 to be used as a facility grounding electrode but, as Dennis states, there is nothing prohibiting a ground rod in the 680.26 bonding.Thanks, I didn't think the bonding was to go to a ground rod.