Sorry wrong replyLast line imply use earth ground as return path but it prohibited in 250
Sorry wrong replyLast line imply use earth ground as return path but it prohibited in 250
The last sentence seem contradict 250 but no actually as pool bonding grid connect egc through other components like pool pump enclosure with egc connectionPlease elaborate on how this relates to the last sentence of 680.26 (B)
Not implied...there are zero restrictions as to what modifications of the rules in Chapters 1-4 that can be made by rules in Chapters 5-7.Implied as
Chapters 1 to 4 basic safety
Chapter 5 to 8 enhance safety
The bonding grid in 680 has nothing to do with anything in 250.4. The words "shall not be required to be extended or attached to remote panel boards, service equipment, or electrodes." can't be any more clear. It's an equi-potential grid, not a fault clearing path.Do you read the last sentence to exempt a pool grounding grid that say for example in your opinion is likely to become energized exemption from 250.4(A)(5)? I think falls short of that.
You saying safety rule 250 bonding to be grounded not required in 680.26(B)?Not implied...there are zero restrictions as to what modifications of the rules in Chapters 1-4 that can be made by rules in Chapters 5-7.
The last sentence seem contradict 250 but no actually as pool bonding grid connect egc through other components like pool pump enclosure with egc connection
That's incidental. If there were no pool pump, etc. there is no equipment ground connected to the pool bonding grid. The pool bonding grid is not a fault clearing path, it is not required to be a fault clearing path, it was never meant to be a fault clearing path. It exists to make a pool safe if a fault is never cleared or the voltage comes from a source other than a fault such as the electric utility.The last sentence seem contradict 250 but no actually as pool bonding grid connect egc through other components like pool pump enclosure with egc connection
What definition of "likely" are you using? Are you likely to win the lottery?is likely to become energized
If no electrical items in and around pool, it generally exempt nec.That's incidental. If there were no pool pump, etc. there is no equipment ground connected to the pool bonding grid. The pool bonding grid is not a fault clearing path, it is not required to be a fault clearing path, it was never meant to be a fault clearing path. It exists to make a pool safe if a fault is never cleared or the voltage comes from a source other than a fault such as the electric utility.
In 'If no electrical items in and around pool, it generally exempt nec ' mean 'If no electrical fittings in and around pool, it generally exempt nec 250'.If no electrical items in and around pool, it generally exempt nec.
Let talk pool with Electrical fittings.
That case
For pool
Equipotential potential grid one system
Grounding system and gfci's another system
Neither system effective without the other.
Without GFCIs and grounding, a ground fault
energize the pool area, potentially compromise the equipotential bonding as it design handle stray currents by neutral to ground voltages
Without the bonding grid, stray voltages create a dangerous gradient between bonded equipment and other surfaces, even with GFCIs in place.
680.26(A) says otherwiseIf no electrical items in and around pool, it generally exempt nec.
680.26(A) Performance.
The equipotential bonding required by 680.26(B) and (C) to reduce voltage gradients in the pool area shall be installed for pools with or without associated electrical equipment related to the pool.
Still contradiction no680.26(A) says otherwise
There is no contradiction, rather there is coordination.Still contradiction no
If with Electrical Equipment, 250 requirement trigger
If without electrical equipment . no relevance to 250, it exempt
250 require a jumper interconnection between these independent systems when a pool has both types of equipment.
I have absolutely no idea of what you are trying to say!Still contradiction no
If with Electrical Equipment, 250 requirement trigger
If without electrical equipment . no relevance to 250, it exempt
Very sorryI have absolutely no idea of what you are trying to say!
You said that pool bonding is not required when there is no electrical equipment associated with the pool. I simply posted the code section that very clearly says pool bonding is always required, even if there is no electrical equipment associated or anywhere near the pool.
MeanIf no electrical items in and around pool, it generally exempt nec.
I not say pool bonding is not required when there is no electrical equipment associated with the pool.'If no electrical fittings in and around pool, it generally exempt nec 250
Over the years there have been several pool related electrical shock incidents, some with fatalities involved, where an equipment grounding conductor had failed, in those incidents the pool grid was energized.What definition of "likely" are you using? Are you likely to win the lottery?
Right we agree then, a standard in ground pool with powered pump and lights 250 applies.If there is energized pool equipment of course 250 applies. But if there is no electricity run to the pool at all 680 still applies.
The grid should not be used in lieu of a 250 sized EGC.It does not say its exempt, or prohibited from being a ground-fault return path.
my opinion as as soon as a ECG is connected to a pool grid the grid is 'likely
become energized', as can be seen by several unfortunate and tragic incidents