Esay
- Rocky mount NC
- Industrial Electrician
Yes, I've used these several times. I suppose you could call it an adapter, but it's actually a lug.6 gauge wire is to large to fit in my current bus bar. Has anyone ever used one of these adapters?
It's a code violation to use it.Ah, the good old suicide cord. Not that code matters, but NFPA 70, section 406.7(B) states, "Connection of Attachment Plugs. Attachment plugs shall be installed so that their prongs, blades, or pins are not energized unless inserted into an energized receptacle or cord connectors. No receptacle shall be installed so as to require the insertion of an energized attachment plug as its source of supply." So, I guess TECHNICALLY that's a code infraction.
Yeah, I don't think we are arguing about that. TBH, I've made AND used them. So, I'm covered as far as code infractions are concerned.It's a code violation to use it.
Not make it.
I've done the generator input without an interlock trick until I did what I said I'd never do.(turned utility on before turning offYeah, I don't think we are arguing about that. TBH, I've made AND used them. So, I'm covered as far as code infractions are concerned.![]()
It looks like they only have them for 30 amps max.Using a EasyStart 368 Soft Starter dropped my starting amps such that my Generator was easily able to handle the initial surge.
No.... I'm not an HVAC guy, but couldn't that be addressed with a large starting capacitor?
Cyanide is hazardous, but has a lot of legitimate uses. A suicide cord does not.Yeah, they make cyanide, too. I'm sure not running out to use that!![]()
See you did have some volts/frequency drop even with a larger unit later in the thread. It takes a pretty good size genset to be able to ride through a motor starting without dropping volts/frequency even if only very briefly.Yeah I have run my 2.5 ton at my old house on an 8kw. But the lights dimmed a bit when the compressor started. And you could see the governor take the throttle wide open foe a few seconds
No, it's always been the Kohler 7.5c61 It's rated 7.5 KW but I sometimes round up. It's from back in the day, and I think they rated them a bit more conservatively then. I loaded it down with 9KW resistive load and it was holding it, and there was still a little throttle to go. During Hurricane Sandy that thing powered my whole house for over a week (not AC or dryer) and two of my neighbors had 120v cords plugged in for lights and refrigeratorSee you did have some volts/frequency drop even with a larger unit later in the thread. It takes a pretty good size genset to be able to ride through a motor starting without dropping volts/frequency even if only very briefly.
utility isn't infinite bus, but is usually more stout than a generator on site will be. Utilities have smaller transformers than what we would typically install as a separately derived system to supply same load. They also often have smaller conductors and sometimes somewhat long distances with those small conductors. Voltage still drops, frequency however doesn't change like it will with a local generator when sudden load change occurs.No, it's always been the Kohler 7.5c61 It's rated 7.5 KW but I sometimes round up. It's from back in the day, and I think they rated them a bit more conservatively then. I loaded it down with 9KW resistive load and it was holding it, and there was still a little throttle to go. During Hurricane Sandy that thing powered my whole house for over a week (not AC or dryer) and two of my neighbors had 120v cords plugged in for lights and refrigerator
Even though it's a good little unit, It doesn't start heavy loads like an infinite buss.
Yeah I guess not infinite bus. Really the entire grid isn't infinite. They have a lot of good reasons for smaller transformers like improving lagging power factor, limiting incident energy, and really most services almost never get close to their rated amperage. And if they do, the duration is very brief.utility isn't infinite bus, but is usually more stout than a generator on site will be. Utilities have smaller transformers than what we would typically install as a separately derived system to supply same load. They also often have smaller conductors and sometimes somewhat long distances with those small conductors. Voltage still drops, frequency however doesn't change like it will with a local generator when sudden load change occurs.
Would there be any possibility of damaging my HVAC unit by only supplying it only 80% of its required start up power requirements? Another concern for me is running my refrigerator, and freezer at the same time, and having the HVAC unit stop, and restart as it gets up to set thermostat temperature.You are on the right track here. Generator will almost always have more voltage sag when starting motor loads than when starting on utility power. This will have somewhat of a soft starter (reduced voltage starting) effect on the motor you are trying to start as well. Keep in mind it will not accelerate as fast as when starting on utility power either.
Other considerations is how much load is already running when attempting to start that AC compressor.
I have a 8000 watt portable generator, haven't had to try to start my 3 ton heat pump with it for several years now. But it will run my 3 ton heat pump. Has difficulty starting before it blows the 30 amp generator breaker if there is much other load running already when you try to start it. But once it is started that heat pump often only draws 6 to maybe 8 amps and there is capacity to run other loads once the heat pump is started.
Have you bought the generator yet? Is there a specific model?Would there be any possibility of damaging my HVAC unit by only supplying it only 80% of its required start up power requirements? Another concern for me is running my refrigerator, and freezer at the same time, and having the HVAC unit stop, and restart as it gets up to set thermostat temperature.
Looking at the specs one issue did come up, I'm not sure if you can unbond it or notWestinghouse
WGen9500DFc 12,500/9,500-Watt Dual Fuel Portable Generator with Remote Start, Transfer Switch Outlet and CO Sensor
It does show in the manual that it can be changed over to a floating neutral. I currently have my generator ground bonded through the neutral bus in the panel.Looking at the specs one issue did come up, I'm not sure if you can unbond it or not