Joethemechanic
Senior Member
- Location
- Hazleton Pa
- Occupation
- Electro-Mechanical Technician. Industrial machinery
I really think it's going to run your AC unit without a problem along with normal lighting, your refrigerator and freezer, tv. radio ect.It does show in the manual that it can be changed over to a floating neutral. I currently have my generator ground bonded through the neutral bus in the panel.
Are you using propane or gasoline?
The only thing is you should really undo the N-G bond at the generator, when hooking it to your house using an interlock. If you leave the generator bonded the equipment grounding conductor running to your generator from the panel will be a parallel neutral path.