I am trying to understand what a ground rod does to enhance safety for a portable generator.
From what I have learned from many of you at this forum, a ground rod installed at a service will help open a utility OCPD if a high voltage conductor lands on the bare neutral conductor.
Also it seems most agree that the ground rod may aid in the dissipation of a lightning strike from the utility system.
Now I install a generator to power an outdoor concert on temporary structures, stage, light towers, control risers (front of house) etc.
Can anyone tell me what the ground rod connected to the generator frame does for us in this situation?
Is it solely for lightning protection and if so how would it help and what is it protecting?
At the voltages the system would be operating (120/208) the ground rod has no chance of operating an OCPD
I am not trying to change the code I would just like to know why we do this instead of doing it because the code says so.
Thanks, Bob
[ August 21, 2003, 09:10 AM: Message edited by: iwire ]
From what I have learned from many of you at this forum, a ground rod installed at a service will help open a utility OCPD if a high voltage conductor lands on the bare neutral conductor.
Also it seems most agree that the ground rod may aid in the dissipation of a lightning strike from the utility system.
Now I install a generator to power an outdoor concert on temporary structures, stage, light towers, control risers (front of house) etc.
Can anyone tell me what the ground rod connected to the generator frame does for us in this situation?
Is it solely for lightning protection and if so how would it help and what is it protecting?
At the voltages the system would be operating (120/208) the ground rod has no chance of operating an OCPD
I am not trying to change the code I would just like to know why we do this instead of doing it because the code says so.
Thanks, Bob