Re: Portable Generators and Ground Rods
iwire wrote;
Dave
[ August 23, 2003, 10:20 PM: Message edited by: websparky ]
iwire wrote;
Bob, I am trying to address your questions above by supplying this information below.Also it seems most agree that the ground rod may aid in the dissipation of a lightning strike from the utility system.
Now I install a generator to power an outdoor concert on temporary structures, stage, light towers, control risers (front of house) etc.
Can anyone tell me what the ground rod connected to the generator frame does for us in this situation?
Is it solely for lightning protection and if so how would it help and what is it protecting?
By adding a ground rod to a generator that is connected to the wiring systems of temporary structures at an outdoor event such as described, it serves to help maintain and equal potential between all connected items in the event of a lightning strike. It does not however provide any additional protection for the actual separately derived electrical system that the generator provides.2000 NFPA 780 Standard for the Installation of Lightning Protection Systems
Appendix L1. Fundamental Principles of Lightning Protection.
The fundamental principle in the protection of life and property against lightning is to provide a means by which a lightning discharge can enter or leave the earth without resulting damage or loss. A low impedance path that the discharge current will follow in preference to all alternative high impedance paths offered by building materials such as wood, brick, tile, stone, or concrete should be offered. When lightning follows the higher impedance paths, damage may be caused by the heat and mechanical forces generated during the passage of the discharge. Most metals, being good electrical conductors, are virtually unaffected by either the heat or the mechanical forces if they are of sufficient size to carry the current that can be expected. The metallic path must be continuous from the ground terminal to the strike termination device. Care should be exercised in the selection of metal conductors to ensure the integrity of the lightning conductor for an extended period. A nonferrous metal such as copper or aluminum will provide, in most atmospheres, a lasting conductor free of the effects of rust or corrosion.
Dave