potable water storage tank

Status
Not open for further replies.

same

New member
A plastic holding tank with 2 bulb floats, each swithing 1 leg of 2 separate 240v/20amp circuits, controling 2 separate pumps.Keep in mind that all of the plumbing is done in PVC pipe up to the pressure pump then it changes to copper on the discharge side and supplies the residience.In this situation 1 of the SJOW cords became frayed and 1 of the wires inside contacted the water and didnt blow the 2 pole 20amp breaker.I didnt realize there was a problem until i touched a brass valve that was a drain for the tank and felt tingle.The copper in the residence is grounded per code.There are no grounds in the SJOW cords, but even there was it would be sealed up in the bulb?Any help would be great.
 
Re: potable water storage tank

Be glad there was no grounds. Make sure you have a good quality flexible cable to the float switches.
 
Re: potable water storage tank

Check the manufacturers installation instructions for the pumps, to see if they require an equipment grounding conductor (If the instructions are not available, look at the factory wiring to see if a ground connection is available). If so you will have to change the non-grounding cords to those pumps. If not as Bennie said use the proper cord for replacement.

Pierre
 