This is the setup.
If you are describing how this system works, I think I am agreeing with this description. If you are describing what you think the NEC has to say about what comprises an "attachment plug," then I do not understand your point. Are you agreeing with my calling this a violation, or not, and what is your reason for seeing it one way or the other?Charlie my understanding is one end is male and the other female. You plud a cord similar to one from a monitor into the wall outlet and plug the other end into the male receptacle in the wall. The other end is reversed.
And IMO that is all that matters [/quote]Ditto.
It is my opinion that the in-wall portion is made of an approved wiring method,
And I agree that the cord portion is not being used as permanent wiring and regardless, it could be across town being used on an electric weed eater at the time of any inspections, it is not part of the in wall wiring. Heck, if I'm around and need an extension cord the one that comes with this product will always be disconnected and re connected, it definitly would not be a permanent connection.and the flexible cord section, with plug and socket, are not being used as a permanent wiring method.
I wanted to discuss this tidbit as well. Al and I and a number of other members had an interesting discussion some time ago on the subject of what is, and what is not, an outlet.
Are these two things "outlets"? To be specific, are they part of the "premises wiring system"? For that matter, is the set of conductors that connects the two a part of the "premises wiring system"? I get the impression from the vendor's web site that they do not consider this to be the case. The two "boxes" (for the moment, I choose not to call them "outlets") are connected to each other by permanent wires and proper terminations. But they are not connected to the circuit breaker or to any other conductors in the house by any permanent means. So does that exclude them from being within the "premises wiring system," or not?
Well, assuming all of this is code compliant, it would seem you could buy the components separately for at least 1/2 the MSRP price or even slightly below their 50% off special ($15 for inlet, $7 for outlet, $2-$3 for the cable pass-through, plus the other common stuff). I've never used any of these so I can't speak to the quality of one over the other. If you don't mind a weather-proof product, you could even get the inlet for about $10 or less from someone like Leviton.Any issues?
Okay. Let's say you want to hang a flat-panel TV on the wall, so you need to install a recessed receptacle in the wall where the TV will be mounted.I would do it within the rules of the NEC and as I am not sure what you are describing that is the best I can answer.
Everyone has a supervisor for a reason, and most jurisdictions have a decision-appealing process.The thing I find funny is it seems the AHJ has already made their position clear and IMO 90.4 gives them the right to turn down a product so nothing we say can change things one way or another.
I have to agree with this.. . . I really don't see any safety issue with this. It is a matter of code interpretation but not safety , IMO.
You want the TV to be supplied, not only by the same circuit as the rest of the system, but by the same multi-outlet surge/noise strip or even UPS.
How would you do it, including more detail than "compliantly," please?
I am in a bit of a quandary over what part of the code covers what part of this installation. I'm just not sure.I wanted to discuss this tidbit as well. Al and I and a number of other members had an interesting discussion some time ago on the subject of what is, and what is not, an outlet.
Are these two things "outlets"? To be specific, are they part of the "premises wiring system"? For that matter, is the set of conductors that connects the two a part of the "premises wiring system"?...
Simple. Let the wires dangle from the TV?s location down to the location of the other components.Okay. Let's say you want to hang a flat-panel TV on the wall, so you need to install a recessed receptacle in the wall where the TV will be mounted. You want the TV to be supplied, not only by the same circuit as the rest of the system, but by the same multi-outlet surge/noise strip or even UPS. How would you do it, including more detail than "compliantly," please?
I do:I don't see anything that restricts that defintion to meaning the male end of an extension cord or a component's power cord.
To me, it's clear that a plug is male and a receptacle is female. The slots of a socket cannot be "inserted in" the blades of an inlet.Attachment Plug (Plug Cap) (Plug). A device that, by
insertion in a receptacle, establishes a connection between
the conductors of the attached flexible cord and the conductors
connected permanently to the receptacle.
Receptacle. A receptacle is a contact device installed at the
outlet for the connection of an attachment plug.
Outlet. A point on the wiring system at which current is
taken to supply utilization equipment.
Receptacle Outlet. An outlet where one or more receptacles
are installed.
I would have to agree with that, other than the in-wall wiring is installed without any oversight whatsoever. We say it is code compliant but then say it is not really under the code so where does that leave the AHJ?Well you make a good point however I really don't see any safety issue with this. It is a matter of code interpretation but not safety , IMO.
It does. What if I used NM as in-wall speaker wiring? Does it now become part of the premises wiring system?But they are not connected to the circuit breaker or to any other conductors in the house by any permanent means. So does that exclude them from being within the "premises wiring system," or not?
Is that a need or a want? I agree it would look a lot better, but so do entertainment centers. Now we just have an entertainment center without the cabinet to cover the ugly parts.Okay. Let's say you want to hang a flat-panel TV on the wall, so you need to install a recessed receptacle in the wall where the TV will be mounted.
You could, but if the wire in the wall is not NEC stuff, how do we say it is compliant with the NEC?I can also argue, as I said before, that since it is not wired to the power of the building then the nec is silent on this issue.
Same with me, and I've been doing this for many more years than these kits have been available, and for far less cost.I believe this is the reason the manufacturers designed this setup.
It's clear to me that an inlet is not an outlet.