junkhound
- Renton, WA
- EE, power electronics specialty
Ok, so basically I've come across conundrum where I have a shaded pole pump motor that draws about 5 to 6 amps when running, yet for the work it does it should only be drawing about 1.6 amps. My question is from those 6 amps how much of that current ends up as waste heat and how much of it is just reactive power? I'm at a loss to explain this exceptionally high current draw.
Good question - realized and am embarrassed that in 7 decades have not thought to ever actually measure one of these little motors.
Just always took them for granted and that as per textbook the efficiency was under 50% and PF under 0.7
So, learn some facts every day.
grabbed an old GE fan motor, 1/6 HP shaded pole, 6.0Amp, 6 pole, 120 Vac 60 Hz motor from the stockroom.
Bench test data:
Unloaded
116.8 Vac
5.32 Amps rms
269 Watts
PF 0.43
Math check: 116.8 * 5.32* .43 = 267W, close, within 1%
Small fan load
116.8 Vac
5.33A rms
294 Watts
PF =0.47
Math check: 293W, within 1%
efficiency = 25Wload/294W = a whopping 8.5% efficiency, not very 'green', eh?
My dynamometer is hooked to a small micro-hydro turbine at the moment, so cannot load the motor for a better load measurement, but 1/6Hp shaft = 124W, so working thru the math the best efficiency would be about 40% full load. PF estimate max about 0.6 full load.