Does a very poor power factor have an effect on voltage drop? If so how much influence does it play and how would one calculate for voltage drop with a poor power factor.
Ken9876 said:Does a very poor power factor have an effect on voltage drop? If so how much influence does it play and how would one calculate for voltage drop with a poor power factor.
Ken9876 said:Does a very poor power factor have an effect on voltage drop? If so how much influence does it play and how would one calculate for voltage drop with a poor power factor.
Rattusrattus said:Simply put, the current drawn by a load is inversely proprotional to the power factor:
I = P/(VxPF)
Where "P" is the real power, "V" is the applied voltage and "PF" is the power factor.
VD = IxZ = PxZ/(VxPF)
where "Z" is the impedance of the line.
For example, a PF of 0.8 would increase the voltage drop by a factor of 1.25.
bob said:Rattus
Your calc I = P/(VxPF) Power = IVxPR is in watts. VD uses VA in the caculation not watts. VD = IRCos(theta) + IXsin(theta).
**** Sample Caculations using R = 2 and X = 0.1 amps = 10 ************* Cos *** Sin *** R *** X *** amps *** VD
0.9 *** 0.017 **2 ***0.1 *** 10 *** 18.017
0.8 *** 0.600 **2 ***0.1 *** 10 ****16.6
0.7 *** 0.700 **2 ***0.1 *** 10 *** 14.7
0.6 *** 0.800 **2 ***0.1 ***10 *** 12.8
0.5 *** 0.870 **2 ***0.1 ***10 *** 10.87
I can not get the spacing correct in these type tables. HELP
rattus said:Of course it is in watts.
Preal = IxVxPF (watts)
I can't make any sense of your equation.
Kingkingpb said:
kingpb said:Bob,
Yes your right, but I thought the discrepancy was over the VA versus the watts. That's why I showed the second equation demonstrating the substitution for "I", orignally posted by Rattus.
rattus said:I finally doped out the equations, and there are two phase angles to consider. One (theta) determines the PF of the load; the other (phi) is the phase angle of the line impedance.
The equation should read,
VD = (Preal/(Vlnxcos(theta)))*(R*cos(phi) + X*sin(phi))
bob said:(Preal/(Vlnxcos(theta))). I think this is = watts/(V x PF) = VA/V = I.
Which looks very much like VD = IRCos(theta) + IXsin(theta).
However theta is the PF angle not line impedance angle.
This simple equation answers the original question...
Smart $ said:It does?
I get the impression, and I may be way off base, that the original question is regarding voltage drop on circuit conductors when loads have a low power factor. Wouldn't the circuit conductors be evaluated as components of the total load upon the source, then VD_load subtracted from V_source to determine VD_conductors?
Just off the top of my head, without performing any calculations to confirm, I'd say the votage drop across the circuit conductors due soley to the power factor of a load thereon would be negligible.
Just wrap CODE tags around the selected text or table, or highlight and click the "#" button on the webpage editor.bob said:I can not get the spacing correct in these type tables. HELP
ramsy said:Anyone care to splain how we differentiate circuit balancing with these formula, since voltage drop varies substantially between such circuits?