rattus said:Now, what do you say to my claim that we have two angles to consider?
First, we have the PF angle of the load itself. That is, arccos(PF)
Second, we have the phase angle of the line itself. That is, arctan(X/R)
I contend that you must use both angles in your formula. If you use only the PF, it falls out of the equation and therefore has no effect on VD.
I say that you return to your text books and check again. This formula
"VD = IRCos(theta) + IXsin(theta)", is in every engineering text that I have
and it is used for VD caculations. The PF does not drop out of the equasion.
Why don't you take the time to check out the IEEE Red book and read their explanation of this caculation. I will say that in real applications that X is small
for short lengths of wire. You can get an accurate result using the actual given line current for the load, VA/V, x the wire resistance.