In the beginning Charlie B. asks what a system of distribution transformers owned by a non-utility entity would look like to serve 2 dozen classroom trailers. The discussion quickly descends into the level of "how many angels can dance on the head of a pin" and he quietly steps away.
The crux of the discussion is "where does the secondary of a transformer physically end and, perhaps, should a secondary be treated as a tap.
here is a summary of the back and forth:
Use Polaris
NEC prohibits Taps
Any wire connected to 2ndary is tap?
Yes 240.21(C) "single load"
No, 2ndary not tap, but often treated as such
No jumper wire -- not permitted indoor xfmr
Use TEE, Polaris busbar
Piece of wire and TEES -- tap[p]ing a tap?
nothing prohibits stacking
2ndary must have OCP before you can tap them
NO read rest of sentence.
OCP required
smaller conductors connected to 2ndardy but not via a single wire.
You can connect as many sets of wires to 2ndary, but not to secondary conductor.
The sections of code that appear to be relevant to me are: 240.21, (B), (B)(5), (C), (C)(4).
Here is what I understand from the Code:
Conductors connected to the secondary lugs of a transformer are feeder wires under (B). They clearly are not branch circuit wires.
Multiple taps to the feeder wires are allowed by (B) and (C).
The taps can be of any length since they are outside according to (B)(5).
The taps are legal under (C)(4).
ARTICLE 240 -- Overcurrent Protection
Part II. Location
240.21 Location in Circuit. Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (H). Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4.
240.21(B) Feeder Taps. Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1) through (B)(5). The provisions of
240.4(B) shall not be permitted for tap conductors.
240.21(B)(5) Outside Taps of Unlimited Length. Where the conductors are located outside of a building or structure, except at the point of load termination, and comply with all of the
following conditions:
(1) The tap conductors are protected from physical damage in an approved manner.
(2) The tap conductors terminate at a single circuit breaker or a single set of fuses that limits the load to the ampacity of the tap conductors. This single overcurrent device shall be permitted to supply any number of additional overcurrent devices on its load side.
(3) The overcurrent device for the tap conductors is an integral part of a disconnecting means or shall be located immediately adjacent thereto.
(4) The disconnecting means for the tap conductors is installed at a readily accessible location complying with one of the following:
a. Outside of a building or structure
b. Inside, nearest the point of entrance of the tap conductors
c. Where installed in accordance with 230.6, nearest the point of entrance of the tap conductors
240.21(C) Transformer Secondary Conductors. A set of conductors feeding a single load, or each set of conductors feeding separate loads, shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (C)(6). The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.
240.21(C)(4) Outside Secondary Conductors. Where the conductors are located outdoors of a building or structure, except at the point of load termination, and comply with all of the following conditions:
(1) The conductors are protected from physical damage in an approved manner.
(2) The conductors terminate at a single circuit breaker or a single set of fuses that limit the load to the ampacity of the conductors. This single overcurrent device shall be permitted to supply any number of additional overcurrent devices on its load side.
(3) The overcurrent device for the conductors is an integral part of a disconnecting means or shall be located immediately adjacent thereto.
(4) The disconnecting means for the conductors is installed at a readily accessible location complying with one of the following:
a. Outside of a building or structure
b. Inside, nearest the point of entrance of the conductors
c. Where installed in accordance with 230.6, nearest the point of entrance of the conductors