171206-1144 EST
The following is something for everyone to chew on.
Parts and meters being played with:
Sq-D 500 VA 60 Hz transfomer. Two 240 V windings, and two 120 V windings. Part # SV1B or something like that. Fluke 27, Beckman 4410, Kill-A-Watt EZ, 100 W incandescent, Superior Electric 7.5 A Powerstat (General Radio name for this is Variac), and a General Radio LRC bridge at DC or 1 kHz.
Fluke R measurements (test leads 0.1 to 0.2 ohms).
X1-X2 = 1.5 ohms, X3-X4 = 1.7 ohms, H1-H4 = 10 ohms.
Note: 1.4 + 1.6 = 3, and 3*4 =12 which is close to 10, good balance.
GR Bridge DC., clip leads 0.2 ohms.
X1-X2 = 1.7 ohms, X3-X4 = 1.8 ohms, H1-H4 = 10.15 ohms.
GR Bridge at 1 kHz, same clip leads. Non tested transformer coils (leads) are open.
H1-H4 L = 1 H, Q = 11.
X1-X2 L = 0.072 H, Q = 10.
X3-X4 L = 0.072 H, Q = 10.
GR Bridge at 1 kHz, same clip leads. Certain transformer leads are shorted.
H1-H4 L = 0.011 H, Q = 2 on Hi-Q range, X1-X2 shorted, X3-X4 open.
H1-H4 L = 0.014 H, Q = 2 on Lo-Q range, X1-X2 shorted, X3-X4 open.
H1-H4 L = 0.024 H, Q = 4 on Hi-Q range, X3-X4 shorted, X1-X2 open.
H1-H4 L = 0.022 H, Q = 3.9 on Lo-Q range, X3-X4 shorted, X1-X2 open.
H1-H4 L = 0.0075 H, Q = 2.4 on Hi-Q range, X1-X2 shorted, X3-X4 shorted.
Did I make any measurement mistakes, don;t know?
Measurements made with the GR Bridge at low signal levels, and 1 kHz may not be close to results at other excitation conditions.
The next experiments are with a 100 W 120 V incandescent alone, and in series with H1-H4 for current limiting.
100 W bulb only.
121 V, 0.82 A, 99.6 W, 99.7 VA, and 0.99 PF.
100 W in series with H1-H4, and no shorted secondaries.
120.8 V, 0.02 A, 1.4 W, 3.0 VA, 0.46 PF. Blub does not glow, bulb is probably about 10 ohms.
Apparent Z looking into H1-H4 = 120.8/0.02 = 6000 ohms. Assuming R is negligible, then calculated L = 6000/377 = 16 H. Magnetic core and flux levels may be the reason for the gross difference.
100 W in series with H1-H4, and X3-X4 shorted, X1-X2 open.
121 V, 0.72 A, 87.2 W, 87.3 VA, 1.0 PF.
Apparent Z looking into series string 121/0.72 = 168 ohms.
Bulb voltage 95.5 V, calculated R = 95.5/0.72 = 132 ohms. bulb is quite bright.
Approximate internal R of transformer is 10 ohms (primary DC resistance) + 4*1.7 = 6.8 ohms (secondary DC resistance reflected to primary), or a total internal seen at the prreimary of 17 ohms.
So equivalent series resistsnce is about 132 + 17 = about 150 ohms.
Estimate of series inductance. Internal resistance voltage drop about 17*0.72 = 12.2 V. Voltage across internal L and R is measured at 26.3 V, and estimate of L drop is sq-root of 26.3*2-12.2*2 = 23.2 V. X sub L is 23.2/0.72 = 32 ohms. Estimated L = 32/377 = 0.09 H. This quite far from 0.02 H. However, the GR bridge and this measurement are under quite different operating conditions. I don't have the time now, but there is a way without a scope to do a better measurement.
You can do some other checks on my calculations, and the results show reasonable correlation.
Others should be starting to provide you some suggestions, but you have to indicate what are your resources.
I have not fully proofread the above.
.