Is it legal by the NEC to install the pigtail with the 10/32 screw on the outside of the switchbox? I realize the screw will not be serviceable, however, it is not a grounding electrode conductor (the GEC is the only bonding I could find that does require serviceability). The apprentice could install these much faster from the outside.
Along the same line of thought: Is it OK to run the EGC out of a mounting hole of a 4-square box and back in through another? For example, 404.8(B)(2) Voltage Between Adjacent Devices requires a barrier in the 4 square box with 2-gang plaster ring. There are conduits on either side of the barrier. Instead of having 2 bonding screws, can I use 1 screw and route a wire around the back of the 4-square to tie together the EGC's?
Along the same line of thought: Is it OK to run the EGC out of a mounting hole of a 4-square box and back in through another? For example, 404.8(B)(2) Voltage Between Adjacent Devices requires a barrier in the 4 square box with 2-gang plaster ring. There are conduits on either side of the barrier. Instead of having 2 bonding screws, can I use 1 screw and route a wire around the back of the 4-square to tie together the EGC's?