First job this morning was to replace SEU o/h service attached to fascia board with 2" mast penetrating the roof.
Original setup was SEU from panel to meter, SEU up wall across soffit to fascia, and GEC leaving the meter base and going to the water pipes.
I replaced the meter base (which wasn't planned; lineman said it was poco requirement for reconnect), put up the mast, and added a ground rod. I took the GEC from the new rod and the GEC from the water pipes and landed them both inside the meter base.
Inspection passed and I left.
HO called and said POCO was refusing to connect because of the water pipe bond. Lineman told HO it was too hazardous, and the HO could get shocked. hmm.
I went back to the job to talk w/ the lineman. He said the poco would not allow the water pipe bond at the service. He said the only thing they will allow to be bonded is a ground rod. hmm.
Lineman suggested I take the ground wire to the panel (fed with seu). hmm.
I asked for permission to install an external intersystem grounding bar on the meter base for the water pipes; access de-nied.
I landed the GEC from the pipes to the ground rod instead.
anyone have an opinion they'd like to share on this policy? Anyone else have a poco with this requirement?
poco was ga power.
Original setup was SEU from panel to meter, SEU up wall across soffit to fascia, and GEC leaving the meter base and going to the water pipes.
I replaced the meter base (which wasn't planned; lineman said it was poco requirement for reconnect), put up the mast, and added a ground rod. I took the GEC from the new rod and the GEC from the water pipes and landed them both inside the meter base.
Inspection passed and I left.
HO called and said POCO was refusing to connect because of the water pipe bond. Lineman told HO it was too hazardous, and the HO could get shocked. hmm.
I went back to the job to talk w/ the lineman. He said the poco would not allow the water pipe bond at the service. He said the only thing they will allow to be bonded is a ground rod. hmm.
Lineman suggested I take the ground wire to the panel (fed with seu). hmm.
I asked for permission to install an external intersystem grounding bar on the meter base for the water pipes; access de-nied.
I landed the GEC from the pipes to the ground rod instead.
anyone have an opinion they'd like to share on this policy? Anyone else have a poco with this requirement?
poco was ga power.