I wanted to follow up with everyone about the status of this job, I pass this inspection on monday, but not before he open every box and check everything, I dont blame him. But he did say something about the circuit breaker from the main box that was use to feed the condesser unit. So I give you guys this question,
If the condesser unit says 35 amps maximum circuit breaker, what size breaker would you use, would you go to 40 like i did, or to thirty like the inspector wanted. Just for information purposes I dont carry 2 pole 35 amp breakers on my truck, and wouldnt the 125 percent rule apply to this