You want to have a technical discussion but you choose to use the wrong terms.
That is your issue not mine.
In this case you are correct, GFCI was the wrong term being 5ma. A submain would be at least 30ma. I choose that term to reiterate the submain would not be an AFCI, my mistake.
I think you know Im referring to: a load center (main breaker if needed) with a primary buss and then secondary buss fed by a GFP breaker.
Here is an example of a load center with a secondary buss:
https://www.google.com/search?q=gen...dlgAYM:;cEAZzYBmqt5CNM:&imgrc=23EaB7ZPdlgAYM:
https://www.google.com/search?q=gen...P6uzsiExwIVgYENCh1dOwCL#imgrc=eg0W1NBLLTOQoM:
http://g-ecx.images-amazon.com/images/G/01/th/aplus/siemens/siemens-GENTFRSWTCH-main-lg.jpg
Now take that 125 amp sub breaker and add 50ma GFP to it.
I have said it before and will say it again.
I would fully support an NEC requirement for GFCI or GFP for every circuit at a branch circuit level in place of the AFCI requirements.
Ok, very good we agree on something
I will always be against GFCI or 30 mA GFP at a main or sub-main level.
Currently the code allows both (sadly not in place of AFCI but in addition to) and there are products available to achieve both.
And as an electrician and installer you have every right to be against that, code should not restrict nor mandate it, but manufactures should offer a sub-main load center as an alternative to achieving GFP protection.
I am saying that cumulative leakage current of the branch circuits and appliances could easily approach the 30mA trip of typical GFP breakers that would be used in a home.
You are 100% correct, however only if done incorrectly. That is why the number of circuits and combined length of cable would be restricted relative to the GFP threshold. That or the threshold would be increased.
This is often why two or more sub-main RCDs are employed so the normal leakage current does not cause nuisance tripping. FWIW when RCDs were first introduced in the 60s and 70s they were so expensive that they were only used as main breakers so as a result a trip threshold of 300, 500 or 1000ma was used. So far the only time any of these device trip is on a genuine fault.
Also, I know you might say 'no North American manufacture could fit more then one submain in a panel without going to a DIN rail" and with that I say not true. Dual split buss panels were common at one point in time
http://www.nachi.org/forum/attachments/f19/47132d1312566462-unknown-object-panel-dscn5736.jpg
https://lh3.googleusercontent.com/A...8zvP-q0oG0F-Zjf28fQrP69pZ40XCQuhS2sGHL4P3Qx0k
https://lh5.googleusercontent.com/c...mdVPNVVrysP8XdBSARMLGhIehVVgtFI9-BodCh4VJDhKA
http://www.nachi.org/forum/attachments/f19/24840d1224962175-need-help-understanding-panel-086.jpg
http://inspectapedia.com/electric/Cutler_Hammer_Panel_2118_BobSissons.jpg
I am saying that even if the cumulative leakage current was 0mA that one random faulty appliance will trip it all and that makes troubleshooting difficult and costly to the homeowner.
True, but that should not stop manufactuers from offering that option. I know others have metioned on ET (shockdoc for one) that if they offered a submain system they would use it.
OK so now we have jumped back out of dwellings and into large buildings with NEC required GFP. GFP that has trip ranges not in mA but in hundreds of amps.
Yes, because a building of that size has a much higher leakage current so the GFP is sized accordingly and in turn correctly. A correctly set GFP does not nusince trip.
The part we seem to be debating is that it is somehow ok for a fault to take out a giant building with emergncy lights that probebly have never been tested but not ok to take out a half dozen circuits in a home. This part I do not get.
I did not say that is unacceptable.
That is acceptable because the trip setting is not 30mA, it is 200, 400, 600, 800 amps and no normal level of leakage current is going to trip it.
Of course, its sized accordingly. So I take it the only concern you have with a submain GFP in resi is that someone might not do it correctly, in that case its the isntaller who is at fault, not the concept. And no we should not disallow something because an idiot can screw it up.
I would never say that, I could find at least a few threads that I have started about going out and troubleshooting this very issue. Sometimes on jobs done by the company I work for.
We do not adjust the breakers until the engineer of record provides the correct settings.
It seems sometimes it takes a customer building going down a few times to motivate the engineer to provide a one line diagram with all the breakers settings. To be fair they typically want the installed feeder lengths before they can do the calculations that is why they are not provided at the start.
And this proves my point: The NEC, manufacturers nor many installer seem to care or see a problem with a main GFP or feel enough concern with taking out more then one circuit.
Yes the building owner is not always pleased about it, but it doesnt stop GFP mains from being used which is my point.
The reason why the NEC allowed this incredibly crude approach was because other methods would add far more cost in the eyes of most builders/electricans (especially back then) to achieve the same without taking down a whole building. Taking down a whole building while inconvinent fulfills practical safegurads at an econimical price without mandating gimmicks. A cheap way to protect everything down stream from an arc fault.
And this leads me to another point:
Decades age when the NEC had a real concern in regards to arcing they made a very simple mandate: just apply GFP. They did not madnate anything more complex, unproven or so forth. Manufacturers came out with the cheapst thing possible: a main GFP.
Random facts? :huh:
All I said in that post was we really do not know what causes the electrical fires being reported.
I could have sworn in another post you mentioned that yourself. :huh:
You are correct, we do not know the cause of residnetial fires in detal.
My point was that when I try to make a point you get bogged down in the small details and how code may say this instead of that.
I agree and why I said those larger GFP breakers have trip ranges well above what you want to protect us from.
Your reading comprehension seems to be falling. :huh:
You claim 30/50ma will nusince trip. When done right it wont.
It might be, it probably is. Of course both of us are guessing with no facts to back it up.
Well there are 3 parts to this.
1. Engineering equations yield deasnet results of the total capacitive coupling in a circuit.
2. Testing can easilly verfiy these theories both for cables and applaicnes.
3. The IEC and foriegn sprkies have enough experince to tell you when at the typical leackage currents for each circuit or set of combined circuits. Ditto for appalinces.
Yes I can deny that a single main GFP for every 6 to 12 circuits is more costly to the homeowner than 6 to 12 individual GFP devices
But not capital cost.
When labor costs for a company run $35 to $50 per hour for warranty work and the hourly rate to a homeowner is $75 to $150 per hour troubleshooting quickly ... very quickly negates the savings per device.
Well it depnds. First consider that faults in properlly wired systems are rare. So the total capital cost saved by employing this on a mjor level is of set by the lesser times service is required. Further, we both know that there are some incredibly cheap buolding methods and contractors who in the end will force the consumer to spend far more money then was saved in the beggining. Does that stop anythin? No. Although in this case I doubt that anology fits well considering my first statment.
You continue to expect your ideas would work flawlessly in the real world even though it is very apparent you have little to no real world experience with the costs associated with troubleshooting randomly tripping circuits.
There not my ideas, more like that of 50 countires totalling billions of people :lol: In so far they all seem content, its only people like you who fight tooth and nail to have more complex, expensive installtions with manufacturer driven CMPs trashing everything. And people like you wonder why everything is so difficult with the excuse 'thats life, go with the flow'
It is the intent to protect the equipment.
Please note the title of the section and look up the definition of equipment in article 100.
Of course its the intent to protect, and it could be done without taking out a whole building, but guess what: practical safe guarding at the lowest cost prevails.
Thankfully you are here to save us all.
Nope, we are all in this togther. One person will be slinced, a dozen people ignored, but if everyone speaks up AFCIs and all the other gimmcks will dissappear over night while the cost of new installations fall.