Hello Pilotpc,
You should read Art 411, it is very short. Because of what Bob wrote (voltage Drop), try to locate the transformer as close to the lighting as possible, and in case you do not have a code book (go get one, there is no excuse), the primary side of your transformer can be protected by a fuse or breaker no larger than 20 amps. Also as Bob mentioned, the wiring method you choose has to be from chapter 3 in the NEC, if you are concealing them or running them in the wall.
Bob
how many installers do you think are using a wiring method from chapter three if they are running the wires through a wall or concealed?
Pierre