we're not planning on using it as an EGC as out cables have the grounds in them. but the customer just sent us this spec asking for the ground in the LFMC. lengths will be roughly 10' max. and most devices are for instrumentation devices, and will be fed back to a wireway to get back to the terminal block enclosures. There are a few 480vac motors and heaters using single conductor SIS pulled thru this LFMC as well.
this is the LFMC that is awaiting the customers approval (3/8" and 1" sizes)
http://flexiblewiringconduits.anacondasealtite.com/Asset/2017 ZHUA.pdf
R-2.3-14
[All cables shall be contained within raceway which shall be Rigid Galvanized Steel (RGS) and liquid
tight metal braided flexible conduit (with grounding wire). Flexible conduit shall not extend more than
three feet without being supported and is only to be used as a final connection to a device and not run
throughout the subassemblies.]