What is the proper (technical) way to crimp a butt splice? >>>



61270.jpg



I have always used this:


Cutter-Stripper-Crimper.jpg




However I am being told its incorrect? :?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
electricians seem to like the plier type tools because they are cheap and fast.

if not done correctly and consistently though, you can have problems which is why most engineers specify a controlled cycle crimper that makes the crimp exactly the same way every time and entirely removes the human variability that would otherwise exist.

https://www.cdw.com/shop/products/P...s_kwcid=AL!4223!3!61836302419!!!g!18283950120!
 

mgookin

Senior Member
Location
Fort Myers, FL
A certified calibrated tool that matches the crimp connector is the "official" way to do it. You'd have to look for listed connectors and find the matching tool.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
What is the proper (technical) way to crimp a butt splice? >>>





However I am being told its incorrect? :?

If the crimp mfgr. requires a certain tool you have to use that. If not I guess as long as you can't pull it apart you're gold.
 

Smart $

Esteemed Member
Location
Ohio
Listed compression-type connectors almost without fail specify one or several crimp tools, which must be used to maintain the listing.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
What I suspected, though I must ask why such a tool needs to cost $350? :eek:

Because it can....
I'll hazard a guess that they really don't sell that many and if you buy one to comply with the requirements you're gonna pay for it.
 

AKElectrician

Senior Member
Up to AHJ IMHO, been places where the name brand crimp must be crimped by the same name brand crimper, don't matter if the lug company specifies another tool that can be used, if it doesn't say the same name brand on both it's a no go. Same place makes you where ice cleats in mud if there is ice on a pond you cant walk too though...
 

mgookin

Senior Member
Location
Fort Myers, FL
Those expensive tools are most commonly used in listed shops. The NRTL inspector wants to see it.

Regardless of what tool you use, if you damage the insulated part, you're a no-go. Part of the requirement of using listed connectors is that you don't damage the insulation.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Oddly, well crimped splices with a $40 crimper seem to hold up just fine, and for years. Sounds more like technical jiber jaber I guess.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Those expensive tools are most commonly used in listed shops. The NRTL inspector wants to see it.

Regardless of what tool you use, if you damage the insulated part, you're a no-go. Part of the requirement of using listed connectors is that you don't damage the insulation.

About the only tools that I see damaging insulation are ones with points on the diye.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Just to get a vigorous discussion going: :)

Do you crimp only the thick metal barrel or do you also crimp the thin section covering the wire insulation?
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
What is the proper (technical) way to crimp a butt splice?

I've always been told that an insulated terminal is squeezed only, not indented. The ones you show, like the common Klein StaKon cutter/crimpers, are for uninsulated. The old "Service Tool II" by then AMP I think, now TE Connectivity TE Connectivity 696202-1, handled those "flag" terminals that folded over the conductor, the other "flag" that folder over the insulation, and the squeeze for the insulated "barrel" crimps.

I think I paid about $40 for mine in the late 80s when I had to make up a dozen or so multipole connectors with the flag crimps.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I've always been told that an insulated terminal is squeezed only, not indented. The ones you show, like the common Klein StaKon cutter/crimpers, are for uninsulated. The old "Service Tool II" by then AMP I think, now TE Connectivity TE Connectivity 696202-1, handled those "flag" terminals that folded over the conductor, the other "flag" that folder over the insulation, and the squeeze for the insulated "barrel" crimps.

I think I paid about $40 for mine in the late 80s when I had to make up a dozen or so multipole connectors with the flag crimps.

Do you have a link for that tool?

My understanding is that the most strippers squeeze rather than indent. Is this not the case?
 

Frank DuVal

Senior Member
Location
Fredericksburg, VA 21 Hours from Winged Horses wi
Occupation
Electrical Contractor, Electrical Engineer

mbrooke

Batteries Included
Location
United States
Occupation
Technician

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired

Attachments

  • ClosedBarrel.jpg
    ClosedBarrel.jpg
    27.4 KB · Views: 5