Hey all, question about some code lingo for you.
My question is in regards to 250.122 (B) Increased Size in which, if we increased the size of ungrounded conductors for the purposes of voltage drop, we are required to increase the size of the EGC proportionately.
I'm working with the 2014 Handbook which has some blue text following the explicit code requirements that gives notes on the code itself and calculation examples.
In this blue text, it says "...where ungrounded conductors are increased in size to compensate for voltage drop... the EGCs must be increased proportionately. In some cases, use of a conductor with a higher insulation temperature rating allows for compliance with ampacity adjustment and correction requirements without having to increase the circular mil area of the conductor.
This underlined section is the portion I'm curious about.
We are demoing an existing sign, extending the run to a new location ~40 ft. away, and installing the feed for a new LED one.
The total length of the run from Panel to New Sign is ~271 ft.
The existing interior conduit run inside the building is 1/2" EMT with an existing 3-wire #12 network handling some other loads.
The existing exterior run is 1/2" Schedule 80 PVC, which will be completely unfilled/empty once the existing feed is removed.
I'm trying to utilize both existing raceways and just extend the existing PVC to the new location to save on cost.
Being mindful of VD and of course project costs, I've calculated that the largest pair of ungrounded conductors I can fit inside the interior 1/2" EMT is 2 x #8 AWG THHN (Hot, Neutral), utilizing the EMT itself as the EGC. I plan to add an EGC conductor for the exterior PVC run to avoid utilizing the earth as a ground-fault return path. Thus, the exterior PVC would contain 3 x #8 AWG THHN wires, which just barely crosses the 40% threshold.
Regarding the above underlined section, how would this apply to me potentially utilizing a slightly smaller EGC such as a #10 AWG, but a different wire type with a higher insulation temperature rating to fulfill conduit fill requirements?
Would I have to match the insulation temperature rating of the required #8 EGC with a different type of wire?
My question is in regards to 250.122 (B) Increased Size in which, if we increased the size of ungrounded conductors for the purposes of voltage drop, we are required to increase the size of the EGC proportionately.
I'm working with the 2014 Handbook which has some blue text following the explicit code requirements that gives notes on the code itself and calculation examples.
In this blue text, it says "...where ungrounded conductors are increased in size to compensate for voltage drop... the EGCs must be increased proportionately. In some cases, use of a conductor with a higher insulation temperature rating allows for compliance with ampacity adjustment and correction requirements without having to increase the circular mil area of the conductor.
This underlined section is the portion I'm curious about.
We are demoing an existing sign, extending the run to a new location ~40 ft. away, and installing the feed for a new LED one.
The total length of the run from Panel to New Sign is ~271 ft.
The existing interior conduit run inside the building is 1/2" EMT with an existing 3-wire #12 network handling some other loads.
The existing exterior run is 1/2" Schedule 80 PVC, which will be completely unfilled/empty once the existing feed is removed.
I'm trying to utilize both existing raceways and just extend the existing PVC to the new location to save on cost.
Being mindful of VD and of course project costs, I've calculated that the largest pair of ungrounded conductors I can fit inside the interior 1/2" EMT is 2 x #8 AWG THHN (Hot, Neutral), utilizing the EMT itself as the EGC. I plan to add an EGC conductor for the exterior PVC run to avoid utilizing the earth as a ground-fault return path. Thus, the exterior PVC would contain 3 x #8 AWG THHN wires, which just barely crosses the 40% threshold.
Regarding the above underlined section, how would this apply to me potentially utilizing a slightly smaller EGC such as a #10 AWG, but a different wire type with a higher insulation temperature rating to fulfill conduit fill requirements?
Would I have to match the insulation temperature rating of the required #8 EGC with a different type of wire?