synchro
Senior Member
- Location
- Chicago, IL
- Occupation
- EE
It appears that 4 #10's would meet the conduit fill requirement. So if you could use that for a MWBC then you could split the 120V loads between the two hots. Not only would that split the load currents between the hots, but their currents would subtract on the neutral. So the voltage drop would be reduced compared to using 3 #10's for a 2-wire 120V circuit.