wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
I think your logic is this: sometimes we can avoid upsizing an ungrounded conductor by using a higher insulation temperature rating. So can we avoid upsizing an EGC by using a higher insulation temperature rating on the EGC? And isn't that what the sentence in the commentary to 250.122(B) is talking about?Where we seem to be in disagreement is whether or not this particular note and the above logic applies to the EGC.
The consensus answer to both questions is no, as everyone has explained. And if you think about it, insulation temperature rating isn't a thing for the EGC. The EGC could, after all, be bare. And under normal conditions, the EGC is not carrying current, so you don't have to worry about the heat it generates damaging its insulation. A higher temperature insulation on the EGC in no way improves its ability to do its job, unlike a circuit conductor.
{I'm ignoring the obvious limitations likes "don't use 60C only insulation on the EGC alongside conductors sized based on 75C or 90C ampacities.]
Cheers, Wayne