Pull box sizing!

Status
Not open for further replies.

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
Hello, Small job turned into a panel replacement. My inspector said he would ding me for a existing pull box that was undersized. I am not technically touching it replacing a panel above it. Want to make sure I am sizing it correctly.

Currently it is 3'x6" I get 3'x16.25" The distance from raceway conductors sharing same conductor will be greater than (2x6) 12" so I was not worried about the Length its more enough I believe.

could not find any exception for nipples since the whole top section is under 2'

See anything wrong with this. going through my book right now. Thank you guys.
 

Attachments

  • conduit.jpg
    conduit.jpg
    1.1 MB · Views: 47
My inspector said he would ding me for a existing pull box that was undersized. I am not technically touching it replacing a panel above it.
Sounds like it shouldn't be involved in the scope of work at all.
 