I hear ya!!! Happy to see a sense of humor!!!!! :thumbsup:just havin some fun have a good one bro
I guess in Argentina red is ground?:lol:
An old hack told me one day, "them wires don't know what color they is"
What is the reason a # 6 is safe to phase tape green and a smaller wire is not? TIA
LOL!!! No comment!! Trust me, the worse I?ve seen was from Cali!!! I actually said this before, and it only took a few minutes before someone else agreed. This isn?t to say all of them>>>obviously, some of the best are on here!!!! Heck, tell the bad ones to stop moving to WA, they are giving Cali a bad rep., and now WA??. LOL!!! We have bad ones here too, and I?m not the best in the world!! But, trust me, I?ve worked with a few from cali, and every time they was wrong and cutting corners!!!
Although you cannot tape grounding wires smaller than #6 with green, you can strip the wire where it is exposed and meet the marking requirement.
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section. Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors.
What is the reason a # 6 is safe to phase tape green and a smaller wire is not? TIA
LOL!!! No comment!! Trust me, the worse I?ve seen was from Cali!!! I actually said this before, and it only took a few minutes before someone else agreed. This isn?t to say all of them>>>obviously, some of the best are on here!!!! Heck, tell the bad ones to stop moving to WA, they are giving Cali a bad rep., and now WA??. LOL!!! We have bad ones here too, and I?m not the best in the world!! But, trust me, I?ve worked with a few from cali, and every time they was wrong and cutting corners!!!
Because when you get into the larger sizes the manufactures only make it in black.
Exactly!! I just looked at my catalog!!That used to be correct, but most wire manufactures now make larger conductors in most colors.
Chris
It's true for most US and Canadian manufacturers; however, most other foreign manufacturers still have a #6 cuttoff - and there are plenty. See the UL Online Certifications Directory , check "Display Guide Information only" and search Category Codes ZLGR and ZKST. Click the link to "guideinfo" and in then the "view listings" in the upper left hand corner.That used to be correct, but most wire manufactures now make larger conductors in most colors.
Chris
It's true for most US and Canadian manufacturers; however, most other foreign manufacturers still have a #6 cuttoff - and there are plenty. See the UL Online Certifications Directory , check "Display Guide Information only" and search Category Codes ZLGR and ZKST. Click the link to "guideinfo" and in then the "view listings" in the upper left hand corner.
There are actually more foreign manufacturers than domestic since wire is one of the easiest electrical building products to market in the US. Several of the larger foreign manufacturers also can make colored conductors #6 and above, but often still don't except as "special" orders. For most of them it still isn't economically justified.
Most of the thermoplastics (Cat Code ZLGR) are pretty easy to make in any color, in any size; however, stocking any color other than black over #6, is up to the distributer. They may feel it isn't worth the inventory space, especially at the "branch" level. If they are closely associated with a major US manufacturer's distribution operation, it is usually available fairly quickly - anyone can get it, but it may take a while. As local demand increases, so does the supply (and stocking).I didn't have all of that information, but I know for a fact that no one around here carry's any colored wire that large. See my tag line if you want to know how to get it.:happyyes:
Exactly!!! <<<<<seems this is my new answer to everythingThey may feel it isn't worth the inventory space, especially at the "branch" level.
Although you cannot tape grounding wires smaller than #6 with green, you can strip the wire where it is exposed and meet the marking requirement.
110.54 Bonding and Equipment Grounding Conductors.
(B) Equipment Grounding Conductors. An equipment
grounding conductor shall be run with circuit conductors
inside the metal raceway or inside the multiconductor cable
jacket. The equipment grounding conductor shall be permitted
to be insulated or bare.
250.119 Identification of Equipment Grounding Conductors.
Unless required elsewhere in this Code, equipment
grounding conductors shall be permitted to be bare,
covered, or insulated.
2011 NEC
I don't know where the idea that stripped wire would appear to be a grounding conductor. I guess it was by analogy to the fact that a #6 or larger wire could be identified by taping a color only at a termination, rather than its entire length. Perhaps my father taught me that in the 1950's (he was an engineer and they as we all know they have strange ideas about wiring).
I do know if I saw a conductor stripped for essentially its full exposed length, I would consider it a grounding wire.
In any event I can find nothing definitive in the code.
Because when you get into the larger sizes the manufactures only make it in black.