This has a 2004 copyright at the bottom. Does this address what you are thinking?
https://www.mikeholt.com/mojonewsarchive/GB-HTML/HTML/The-Grounding-Truth~20040602.php
Very nice MAC. That TN system that Norway uses is exactly what we used in hospital OR's. The equipment grounds and neutrals were left separate- not bonded. The pros to that system is that you can not get shocked through grounded metal parts. The cons is that it won't clear a fault either, as faulted current can't jump back to the neutral and trip a breaker. They use some sort of extra monitoring devices that I didn't get a chance to further explore- a third party calibrated the special equipment.
Even then, that doesn't have to do with a GES. That has to do with bonding the non-current carrying metal likely to become energized with the neutral to clear a fault.
That engineer emailing Mike Holt states in his conclusion:
- [FONT=Arial, Helvetica, sans-serif]The grounding of the distribution system is NOT NECESSARY for the system itself; it's only useful when providing protection against lightning. The line voltage protections should be referred to the neutral or common point, a line that should be provided even if not needed for the distribution itself.[/FONT]
[/FONT]While ground rods protect against lightning they can also carry current in a fault to earth though this is not their intended use- the earth has too much resistance to clear a fault. It's also why we only have to size our ground rod GEC's to #6. You can have a 40 story building with a 4000 amp 480v service and you still will only need #6 to ground rods. Bonding to water pipe as GE we follow 250.66 because we have to consider the service potentially energizing the water pipes.
Maybe I'm off base in a matter of semantics.
The purpose of grounding (to earth) our electrical systems is for lightning, static, and other foreign voltages. A water pipe is exceptional as it can run along with the electrical system throughout the building and is to be apart of the GEC system. But a ground rods purpose is NOT to clear faults or protect against shock from our systems.