Who uses push in wire connectors and how do you like them?
any problems? Benefits?
any problems? Benefits?
What are they? Got a pic?Who uses push in wire connectors and how do you like them?
any problems? Benefits?
Trying to upload pic but can’t.What are they? Got a pic?
Thanks for trying. Appreciated.Trying to upload pic but can’t.
How'd you do that?
How'd you do that?
Anyway ...I asked because I've used them a few times and they seem too easy to be good, but they hold tight
Ok. That’s my first problem. I do everything on my phone. I haven’t used a computer in a while, only because I’m always on the run.Try this, find a photo on a website, right click on the photo and select "copy image location". In the forum reply box type.![]()
![]()
I like those for changing out old ballasts in fixtures other than that it's twist and wirenut for me.
Ok. That’s my first problem. I do everything on my phone. I haven’t used a computer in a while, only because I’m always on the run.
But thanx.
Key word is almost. They are much better at assuring contact than the backstab connections on switches/receptacles, plus you are not straining said connection like you do when you push a backstabbed device into the box. How well will they handle a 15-20 amp load for extended time, IDK. Would suspect they can't be any worse than a cheap grade switch/receptacle's ability to handle the same load though.Almost like back stabbing a, never mind.
I prefer not to use them for two reasons.
First. On hot, humid days my sweaty, greasy hands can't grip the wire jacket firmly enough for me to feel the wire bottoming in the "wago". I can't "feel" if my hand is slipping because of lack of grip or because I'm bottomed. If I'm on a service call for a recess can ballast in a hot soffit, I want a good connection so no return trip.
I definitely can "feel" when wirenuts bite into the copper. They make wagos clear to verify the connection. Its hard to see the wire bottomed in the translucent wago in the recess can make-up box from outside the hardlid on a sunny day.
Two. I saw a wago failure in a (television display) plugmold endfeed. What a mess. Could not handle 20 amps or however many TV's they had.
For dead ending wires they're OK. For fixture connects, I'm cool with the apprentices using them. But I don't carry any on the service truck.
Key word is almost. They are much better at assuring contact than the backstab connections on switches/receptacles, plus you are not straining said connection like you do when you push a backstabbed device into the box. How well will they handle a 15-20 amp load for extended time, IDK. Would suspect they can't be any worse than a cheap grade switch/receptacle's ability to handle the same load though.