journeyman0217
- Tennessee
- Electrician
is there any issues by putting an outdoor gfci receptacle on a switch controlled from indoors?
210.52 Dwelling Unit Receptacle Outlets. This section
provides requirements for 125-volt, 15- and 20-ampere receptacle
outlets. The receptacles required by this section
shall be in addition to any receptacle that is:
(1) Part of a luminaire or appliance, or
(2) Controlled by a wall switch in accordance with
210.70(A)(1), Exception No. 1, or
(3) Located within cabinets or cupboards, or
(4) Located more than 1.7 m (51⁄2 ft) above the floor
Assuming the switch is a standard snap switch, in general not a problem.
Just curious if it is not a snap switch or is not "In general" what could be an issue?
When can you not have a GFCI receptacle controlled by any switch?
I thought those were only those used in construction temporary wiring, not any used for building wiring.And there is the fact some GFCIs go to the trip position when powered off.
Dimmer switch and the section Dennis posted.
404.13(E) Dimmer Switches. General-use dimmer switches shall
be used only to control permanently installed incandescent
luminaires unless listed for the control of other loads and
installed accordingly.
I believe you can have a dimmer switch to control a receptacle as long as the receptacle is a listed one for the purpose. Lutron makes them
Seen one a long time ago that was a part of a listed cordset, I'd guess if found a replacement it would be higher cost then a regular GFCI receptacle.I doubt you will find them in standard receptacle design. I believe someone from the forum was trying to find a standard receptacle style gfci that would trip when the power went off but he had no luck.
Good answers in this thread. There is one other domino that falls if the indoor switch is in a room or area called out by 2014 NEC 210.12, the circuit supplying the outdoor GFCI must have AFCI protection.is there any issues by putting an outdoor gfci receptacle on a switch controlled from indoors?
Seems I have seen or heard of a self testing GFI receptacle. (maybe even required by code) anybody else see or heard of that?
I am very aware of the difference, I just mentioned it.And, to be clear, self test is different than trip-on-power-loss being discussed in this thread.