PVC Above ceiling grid

Status
Not open for further replies.

dnbob

Senior Member
Location
Rochester, MN
Can I run a water bond pvc conduit above a grid ceiling.

I cannot find a reference that restricts the use
of pvc above a grid ceiling. The building is precast including the roof, and steeel stud side walls.

Thanks,
Bob
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: PVC Above ceiling grid

I would agree with Hess but would add that if the conductor were #6AWG or larger, run with and secured to the building structure and not subject to physical damage than it can run without any conduit at all.
 