TeddyAdkins
Member
- Location
- WV
- Occupation
- Industrial Electrician
I work as a steel mill electrician but I bought my first house and it currently has a 100 Amp screw in fuse service. I'm going to upgrade it to a 200A service and have bought the materials but I've nevee personally done a service before. Some guys I work with have installed many services and are going to help me but we're not positive if I can use the PVC I purchased going up from the socket to the loop.
I bought aluminum 4/0 and 2 inch sch 40 PVC. The incoming wires are being supported by an anchor/insulator in the brick so the PVC doesn't need to hold the load of the conductors.
So can I run 2 inch sch 40 PVC up my house or do I need emt?
(The hub for the meter is metal, with a male connector and pipe glue I can use that hub right? Or do I need a plastic hub as well?)
I bought aluminum 4/0 and 2 inch sch 40 PVC. The incoming wires are being supported by an anchor/insulator in the brick so the PVC doesn't need to hold the load of the conductors.
So can I run 2 inch sch 40 PVC up my house or do I need emt?
(The hub for the meter is metal, with a male connector and pipe glue I can use that hub right? Or do I need a plastic hub as well?)