I would definitely fail that. With Concrete cover? Maybe if it was a little deeper.Hoping this works.
View attachment 2564476
I would definitely fail that. With Concrete cover? Maybe if it was a little deeper.Hoping this works.
View attachment 2564476
What if it was under the edge of the concrete the entire way?I would definitely fail that. With Concrete cover? Maybe if it was a little deeper.
Probably ok, it would afford protection like under a building slab. 2” of concrete is supposedly equal to one foot of dirt, so if he had dug down deeper, and poured concrete, I would have been ok with it. (Inspector’s discretion)What if it was under the edge of the concrete the entire way?
2" concrete = 1 foot of dirt?Probably ok, it would afford protection like under a building slab. 2” of concrete is supposedly equal to one foot of dirt, so if he had dug down deeper, and poured concrete, I would have been ok with it. (Inspector’s discretion)
I would agree, but that seems to be the rule of thumb.2" concrete = 1 foot of dirt?
seems to me 2" concrete is just plain and simple enough of a shield to protect it from damage - from hand tools or smaller powered tools. Some larger mechanical excavation equipment still has no problem damaging it though, but also has no problem when buried at T300.5 depths with no concrete as well.
It's not an equivalent, it's just an alternative. You can't combine 1" of concrete and 6" of dirt.2” of concrete is supposedly equal to one foot of dirt ...
Correct. If the circuit is under 20 amps and 150 volts, gfci protected, the depth can be reduced to 6”. 12” under other conditions.It's not an equivalent, it's just an alternative. You can't combine 1" of concrete and 6" of dirt.
so a GFCI is also equivalent to 12 inches of dirt thenCorrect. If the circuit is under 20 amps and 150 volts, gfci protected, the depth can be reduced to 6”. 12” under other conditions.
NEC 300.5
If the EC went under the edge of the sidewalk I would be OK with it.What if it was under the edge of the concrete the entire way?
LOL! That’s what 300.5 says!so a GFCI is also equivalent to 12 inches of dirt then
Only place I haven't been able to dig was the Bahamas, some places had granite deposits, all we got was dust when the backhoe scratched it.Having worked in South Fl the argument that it's to hard to dig is hogwash.
Just blast out the pool possibly apply a seal coating and pool is done? Other than piping, equipotential bonding and such, which sounds like a challenge as well.The Dominican Republic is pretty rocky, I had to dig in some landscape lights for the palm trees in the back yard. Only a couple of inches of soil. They must have blasted to build the pool.
Think of the material savings!The Dominican Republic is pretty rocky, I had to dig in some landscape lights for the palm trees in the back yard. Only a couple of inches of soil. They must have blasted to build the pool.
Only at dwelling unitsso a GFCI is also equivalent to 12 inches of dirt then
Is RMC permitted to simply be ran on surface like grass without cover? I'm encountering such a situation currentlyYou are correct in failing the job. Why does he think he can get by with 4" trench when it should be 18" to the pipe. If he didn't want to dig then he should have used rigid or pvc coated rigid.