Is PVC conduit allowed to penetrate a block wall that has a 3 Hour fire rating? I'm thinking not but don't have IBC.
If you use a rated through penetration system with a 3 hour rating then you can.
Chris
Is PVC conduit allowed to penetrate a block wall that has a 3 Hour fire rating? I'm thinking not but don't have IBC.
Sure, as long as the penetration has the required rating.
That means, you'll have to use one of those collars that expand as the PVC melts so the fire rating is still maintained.
Contact the manufacturer you are planning on using such as Hilti or 3M and tell them what you are planning, they will provide the back up for their particular assembly. With out the back up to the products application you will have nothing. You can also find the information in the UL Orange books but it is easier to get it from the manufacturer.Ok do I need to use a collar on both sides of the wall or just one side?
Contact the manufacturer you are planning on using such as Hilti or 3M and tell them what you are planning, they will provide the back up for their particular assembly. With out the back up to the products application you will have nothing. You can also find the information in the UL Orange books but it is easier to get it from the manufacturer.