PVC to EMT

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
Any reason to not use a set screw adapter typically used for flex, to transition from PVC to EMT? It fits fine, would be secure, and no bonding needed, I have EGC inside, and the EMT is bonded on the far end.
 

Attachments

  • 17744780196866801798535315246073.jpg
    17744780196866801798535315246073.jpg
    939.3 KB · Views: 5
Like Hal said they make the proper fittings to transition from one to the other. Although the fitting in the photo may work that isn't it.
 
Note both of these ideas are not acceptable to some AHJs as the male threads of the connector have not been evaluated for use with female threads.
Do you mean the threads have not been evaluated for mechanical connectivity as opposed to electrical/ground continuity or is watertightness the issue?
But if listed materials are not required isn't it up to the AHJ.
 