Because it's made for flex. Use a male threaded PVC adapter glued on>threaded coupling>EMT connector.Any reason to not use a set screw adapter typically used for flex,
Why not a female PVC adapter and a connector?Because it's made for flex. Use a male threaded PVC adapter glued on>threaded coupling>EMT connector.
-Hal
Do you mean the threads have not been evaluated for mechanical connectivity as opposed to electrical/ground continuity or is watertightness the issue?Note both of these ideas are not acceptable to some AHJs as the male threads of the connector have not been evaluated for use with female threads.
358.6: "EMT, factory elbows, and associated fittings shall be listed."But if listed materials are not required
That looks like its for ENT not PVC.View attachment 2582510This is listed for the purpose