I see table 690.31(A)(3)(1) showing PVC wire with a higher amperage than I expected. We're still on the 2017 code here, so haven't delved into the most recent code much & first time I noticed this table. Easy going inspector on the job I intend to use this on, so he'll be fine with complying with a more recent edition of the code. But if I use the following wire, in size #10, am I right in thinking that this is good for 46 amps!?
servicewire.com/Products/XH-PVC.htm
It will be terminated with MC4 connectors on each side that is rated for 54 amps for #10 wire. So I think I'm good for derating the heck out of this with a crowded conduit and all. Just want to make sure I am reading this table right and starting with the right number for my derating. Just higher than the 40 amps for #10 USE-2 I would usually use.
Thanks!
servicewire.com/Products/XH-PVC.htm
It will be terminated with MC4 connectors on each side that is rated for 54 amps for #10 wire. So I think I'm good for derating the heck out of this with a crowded conduit and all. Just want to make sure I am reading this table right and starting with the right number for my derating. Just higher than the 40 amps for #10 USE-2 I would usually use.