Hi,
I’m wiring up a kitchen and I decided to go with 15A split receptacles (if I was going to start over I’d probably do 20A but it’s too late for that - many kitchen receptacles are in exterior walls that are already insulated).
I have an EATON panel and was planning on using DNPL215215 breakers (Non-Common trip with just a handle tie do the split breakers), however I came across the “common trip” requirement and I’m trying to understand if that applies to kitchen receptacles under the current code?
Am I also correct that any 240V circuits that require a neutral will also require a common trip breaker? And conversely 240V circuits with no neutral do not require common trip?
The reason I’m asking all this is I’m am running a bit short of space on my panel and without the ability to use a non-common trip breakers I might have to take some additional steps (such as combining a few circuits - no drywall yet so I have options to run extra wire) to reduce overall circuit count.
Thanks for any help and suggestions on ways to address my shortage of panel space (please don’t suggest adding a subpanel, that’s my least preferred option)
I’m wiring up a kitchen and I decided to go with 15A split receptacles (if I was going to start over I’d probably do 20A but it’s too late for that - many kitchen receptacles are in exterior walls that are already insulated).
I have an EATON panel and was planning on using DNPL215215 breakers (Non-Common trip with just a handle tie do the split breakers), however I came across the “common trip” requirement and I’m trying to understand if that applies to kitchen receptacles under the current code?
Am I also correct that any 240V circuits that require a neutral will also require a common trip breaker? And conversely 240V circuits with no neutral do not require common trip?
The reason I’m asking all this is I’m am running a bit short of space on my panel and without the ability to use a non-common trip breakers I might have to take some additional steps (such as combining a few circuits - no drywall yet so I have options to run extra wire) to reduce overall circuit count.
Thanks for any help and suggestions on ways to address my shortage of panel space (please don’t suggest adding a subpanel, that’s my least preferred option)