Question on upsizing conductors
Im missing something in the count. 2-30 amp and 4 20 amp circuits if all single pole would be 12 ccc not 14 right. If the system is single phase, run them as multiwire branch circuits on a 2 pole 30 and 2-2 pole 20s. Now youd be at 6 ccc (neutrals carrying unbalanced load dont count) and only have to derate to 80 percent.
Sent from my SM-G935P using Tapatalk
The system is a 4 wire 3 phase wye 120/208 and I am using
Two 30 amp breakers which are 2 pole............equals 6 ccc
Four 20 amp breakers which are single pole.....equals 8 ccc
for a total of 14. Is that correct?
if i were to use a double pole breaker for the 20 amps and share neutrals I could get down to ten ccc but that still puts me at 50% derating.
For a 208Y/120 volt system a 3 wire MWBC would be considered 3 CCC's.
Yes but if i used a double pole 20 amp breaker instead of two 20 amp single pole breakers...I could share a neutral and have two less CCC's....so that would put me at 12?
Yes that's correct, initially you said 10 but either way, 10 or 12 you're still at 50%. :)
OK, say a 30 amp double pole breaker is handle tied to a 20 amp single pole breaker on the third phase. Then the 3 ungrounded conductors could be run with a single 30 amp neutral as an MWBC that counts as only 3 CCCs. Any problem with that?
If not, do that twice, and use a double pole 20 amp breaker with a 20 amp neutral for another MWBC. That makes only 9 CCCs, so 70% derating would apply.
Cheers, Wayne
No that's not correct. You got it right earlier. Must have a 4-wire mwbc before the neutral don't count.
No problems with splicing inside the panel? I would think that would violate the neat and workmanlike manner.
Then make the splice in a neat and workmanlike manner.
What is the load on the 30 amp circuit? 15 and 20 amp circuits with general use receptacles might need to be counted as 15 or 20 amps when figuring ampacity adjustments. 30 amp circuits are not so much general use and you may be able to count the actual load instead of full 30 amps - 27.5 amps of load only needs 8 AWG instead of 6 AWG @ 50% adjustment of 90C values. If no receptacle outlet on the circuit - then you definitely only need to look at the connected load.
Cheers, Wayne
Just adding a handle tie won't do it. You would have to re-wire the circuits and abandon the extra neutrals; even though that would work electrically I'm not sure it satisfies 210.4(C) ex. 2 because the handle ties do not the breaker a common trip.
Yeah, it looks like 210.4(C) exception 2 is stricter than necessary. It seems like it should be enough for all ungrounded conductors serving a single piece of equipment to open simultaneously, which the double pole/single pole handle tied together would achieve in the OP's load case.
If the OP can install (2) 20 amp single pole OCPDs at the load end, then my idea would still work using a 30 amp 3 pole breaker.
Cheers, Wayne
Which part is not correct? If he goes from the original 4-20 amp 2 wire circuits (8 CCC's) to two 3-wire MWBC's he still has the 4 circuits but ends up with 6 CCC's then add the 6 CCC's for the two 30 amp circuits he ends up with 12 CCC's.
You must count the neutral unless it is full house-- one neutral and 3 hots. If you have two hots and one neutral then you have to count the neutral. Of course, I am assuming linear loads.
310.15 (B)(4)...Three phase wye connected system and circuit with 2 ungrounded conductors and a neutral you still count neutral as a ccc.
You have to count the neutral of a 3-wire circuit on a 208/120 system. While it meets the definition of a multiwire branch circuit, the neutral "discount" only applies to a full boat [310.15(B)(5)(b)].