The situation without a long backstory:
One raceway with 10 current carrying conductors. Taking into account derating the conductors at 50% ampacity they will have to be upsized. Problem is then my conductors are one size too large for their circuit breakers.
I'm pretty sure it is not possible to use the smaller size conductor from the breakers to enter a box, gutter, or wire way, and then at that point go to the correct size conductors so that they then can all run in the same conduit. This would be a violation correct?