Swbd is an equipment how can it be structure? It is manifactured.
Sent from my SM-G935U using Tapatalk
Ok, now what is the equipment hung on/sitting on/mounted to??
Swbd is an equipment how can it be structure? It is manifactured.
Sent from my SM-G935U using Tapatalk
Conceret pad ahh ja thats structure but thats not where existing electrodes are at in switchboard. I am so confused. How can bdlg and swbd be two different structure. Swbd by itself is equipment.Ok, now what is the equipment hung on/sitting on/mounted to??
Conceret pad ahh ja thats structure but thats not where existing electrodes are at in switchboard. I am so confused. How can bdlg and swbd be two different structure. Swbd by itself is equipment.
Sent from my SM-G935U using Tapatalk
Conceret pad ahh ja thats structure but thats not where existing electrodes are at in switchboard. I am so confused. How can bdlg and swbd be two different structure. Swbd by itself is equipment.Sent from my SM-G935U using Tapatalk
“I have existing switchboard outside building with incoming utility and grounding electrode approximately 10 to 20 feet from building. From the switchboard I have one feeder going into Panel A inside building about 180 feet from existing switchboard. Do I need to have ground electrodes at Panel A inside building per Nec 2014 Article 250.32?”
Sent from my SM-G935U using Tapatalk
You got it all wrong. Panel A to switchboard is 200 feet. The switchboard is grounded has service electrode system. Panel A is located inside the building. From building exterior to switchboard is 20 feet.you added a detail that the switchboard is 10 to 20 feet from the building where panel A is located. In a thread that got closed because it was a duplicate posting of the same question
Lets say just for the point of discussion the switchboard is equipment and no structure at this outside switchgear that the NEC has concern for.
You state that the switchgear has a grounding electrode system installed. And lets say that from an NEC prospective there is no requirement for that grounding electrode.
You take a feeder to a building that clearly is being feed from service equipment at the switchboard
Why would the building where panel A is, be allowed to eliminate a required grounding electrode system
If you installed a grounding electrode system at a equipment that wasn't required by code, you could not eliminate a grounding electrode system at a building that is required by code.
Keep in mind I am working from the 2008 NEC, is their a code change that the building where panel A is at, no longer has to have a grounding electrode system?
Also keep in mind i am not stating there is no structure where the switchboard is located, i will let others discus that issue with you
you added a detail that the switchboard is 10 to 20 feet from the building where panel A is located. In a thread that got closed because it was a duplicate posting of the same question
You got it all wrong. Panel A to switchboard is 200 feet. The switchboard is grounded has service electrode system. Panel A is located inside the building. From building exterior to switchboard is 20 feet.
Sent from my SM-G935U using Tapatalk
Thread that was closed:You read what i said to mean panel a and the switchboard are twenty feet from each other that is not what i was saying maybe i should have said it better.
you added a detail that the switchboard is 10 to 20 feet from the building that panel A is located in. In a thread that got closed because it was a duplicate posting of the same question
You got it all wrong. Panel A to switchboard is 200 feet. The switchboard is grounded has service electrode system. Panel A is located inside the building. From building exterior to switchboard is 20 feet.
Sent from my SM-G935U using Tapatalk
You got it all wrong. Panel A to switchboard is 200 feet. Sent from my SM-G935U using Tapatalk
You got it all wrong. The switchboard is grounded has service electrode system. Sent from my SM-G935U using Tapatalk
You got it all wrong. Panel A is located inside the building Sent from my SM-G935U using Tapatalk
You got it all wrong. From building exterior to switchboard is 20 feet.Sent from my SM-G935U using Tapatalk
Thread that was closed:
"I have existing switchboard outside building with incoming utility and grounding electrode approximately 10 to 20 feet from building. From the switchboard I have one feeder going into Panel A inside building about 180 feet from existing switchboard.
Do I need to have ground electrodes at Panel A inside building per Nec 2014 Article 250.32?"
So we do need GE at Panel A?
Sent from my SM-G935U using Tapatalk
Do I need to have ground electrodes at Panel A inside building per Nec 2014 Article 250.32?"
So we do need GE at Panel A?
Sent from my SM-G935U using Tapatalk