questionable install?

Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
I am looking at a project where the original install shows a freezer 208V and two 120V-20A duplex outlets from a small sub-panel and the panel also has a branch circuit to a outdoor receptacle, when they lose power they plug in a small generator to the receptacle to back-feed the panel to keep the freezer running? my concern is how do you ground a system like this I thought you could not connect a portable generator to a premise wiring system? I did not see a ground rod near the outdoor receptacle but assume you would need something to ground the frame to at least? I will try to get a picture next time I am out there.
 
There is no code compliant, power company compliant, safe way to backfeed a receptacle with a generator.

They need a proper 'inlet' and transfer means.

Do not do what they are asking, you could kill linemen.
 
GREAT comment!

GREAT comment!

. . . Do not do what they are asking, you could kill linemen.
GREAT comment!
thanks Bob
icon14.gif
 
A lot of people do that not understanding that feeding a transformer on the secondary side sends primary voltage down the powerlines. As Bob and Charlie said very dangerous! And in total violation.
 
And just in case your client might be thinking that the ?you could kill linemen? statement is a mere ?the sky is falling? exaggeration, let me invite your attention to,
? 406.6(B) ? the prongs of a cord are not allowed to be energized except by being inserted into a receptacle, and you can?t energize a receptacle by inserting a plug, and
? 702.6, last paragraph and the exception ? you must use transfer equipment, and your client?s situation does not meet the exception.
 
Note that with small changes, this could be a proper install.

1) Proper transfer means could be as simple as a mechanical interlock system between the main breaker of the panel and the 'generator breaker'.

2) A proper 'inlet' can be had that mounts as easily as an ordinary receptacle. The inlet will have prongs sticking out rather than slots for the prongs to go into.

3) The transfer means does not switch the EGC, and does not need to switch the neutral. The building ground system can provide grounding and bonding for the generator.

-Jon
 
Guru, you don't even need to pay $100. You can buy the rocker interlock and assemble your own panel for about half of that. I've made whole-house panels that way for smaller homes.
 