Here is the scope of the project: Using 2-2-2-4 Aluminum XHHW SE-R cable for sub panel board in dwelling unit attached garage feeder from house main sub panel board. The cable will be routed through framing members of the basement ceiling, garage walls and "attic" area and through insulation.
100 Definitions - Feeder
Table 310.15(B)(7)
338.10(B)
338.10(4)(a)
In conclusion for this installation the SE-R cable needs to be installed like NM cable using all the same rules. Because it is installed though insulation it has to be protected by an 80 amp breaker.
Please correct or comment on any area that needs it.
Another question: How do most of you feel about using aluminum wire? I have personally not used much to date. It seems SE-R is mainly sold in aluminum and according to some of the information on the manufactures websites this is not the same aluminum from the 1950s that gave aluminum wire a bad name.
100 Definitions - Feeder
- By definition this is what the 2-2-2-4 from the main panel board in the house to the sub panel board is the garage would be.
Table 310.15(B)(7)
- States can normally be used to size dwelling unit feeders. Here it states for this purpose #2 aluminum is rated at 100 amps. (XHHW is listed, planning to use SE-R cable).
338.10(B)
- States SE-R cable can be used as a feeder
338.10(4)(a)
- States when SE cable is used for interior wiring part II of article 334 (NM cable) excluding 334.80 must be used. (Will be used for interior wiring along complete run).
- 334 - NM cables
- 334.30 - Securing and Supporting. Within 12 in. of every box.
- 334.30(a) - Horizontal runs through holes and notches. Support every 4.5'
- Service Entrance Cable. Interior installations - States where installed through thermal insultaion the 60?C conductor temperature rating must be used. (For this installation it will be in insulation).
- States #2 aluminum is rated for 75 amps @ 60?C
- States the next highest standard breaker size can be used.
- 75 amps is not a standard size, 80 amps is the next standard size.
In conclusion for this installation the SE-R cable needs to be installed like NM cable using all the same rules. Because it is installed though insulation it has to be protected by an 80 amp breaker.
Please correct or comment on any area that needs it.
Another question: How do most of you feel about using aluminum wire? I have personally not used much to date. It seems SE-R is mainly sold in aluminum and according to some of the information on the manufactures websites this is not the same aluminum from the 1950s that gave aluminum wire a bad name.