That is correct, the attached garage general lighting load is already covered by the general lighting calculations (for service calculations). Now we want to run a feeder to supply this garage that already has a zero general lighting calculation already included in the service load calculation, how do we calculate the load for the feeder?
500 square feet x 0 VA = 0. Guess we don't need conductors for the feeder if all that is supplied is general lighting circuits.
How do we determine load for any circuit in a dwelling that would supply loads in the areas we don't need to include in the square footage mentioned in 220.12?