Yes, I did note the comment about learning.Why would you want us to learn a falsehood?
Interesting I thought in that it was directed at someone with 40 years experience by someone who appears to have none........
See post #155.I want you to learn that energy saving by voltage reduction method depends not only on the reduction in internal losses of the motor but also on the reduction in the motor output (and hence reduction in water output in case of pump).If the case study in post #151 does not convince you of that, nothing else can.
Bear in mind also that it is 25% of a motor running at 30% load in the first place.I calculate that less than 25% of the energy savings in post #151 is due to the reduction in motor RPM (directly from the "affinity law" that you point to so much - the relative difference in the cube of the two rpms). While not an insignificant amount, it is a minority of the power saved. Other effects produced 3x the power reduction of that due to the rpm reduction. Not a very good counter example.
Can you point to a single post in this thread that would dispute what I made bold above? Not one of us has claimed a reduction in current would result if a fully loaded motor has it's voltage reduced.
Again, going back in this thread you tried to claim a reduction in voltage to a motor always increases the current.
You were shown otherwise and are now trying to change the subject.
Your objection is not in order:we are trying see whether any energy saving is there by connecting a suitable PFC capacitor across a pump motor;I started with a premise that there will be an increase in motor current with a decrease in voltage across it.That we all accept now that this is so,when the motor is near full load.I hope we may proceed further from that point.
That you still do not grasp that the speed of the INDUCTION motor drops significantly with drop in voltage amazes me.The torque of the motor is directly proportional to the SQUARE of the applied voltage and from the torque-speed characteristic of the motor,you can easily see how greatly the speed is reduced for reduction in voltage.Yes, I did note the comment about learning.
Why not just say you were wrong?
I think half of your experience,I am having is enough to counter your statements.Interesting I thought in that it was directed at someone with 40 years experience by someone who appears to have none........
See post#166.Why would you want us to learn a falsehood?
I ought to be equally amazed that you insist on that but, rather sadly, I'm not. It's just plain wrong.That you still do not grasp that the speed of the INDUCTION motor drops significantly with drop in voltage amazes me.
Your posts on this subject suggest otherwise.I think half of your experience,
See below.I ought to be equally amazed that you insist on that but, rather sadly, I'm not. It's just plain wrong.
Here are curves for an actual motor where we provided the control equipment. It shows performance at rated voltage and 80% of rated voltage.
Look very carefully at the torque curves for the two voltages.
How much speed difference can you discern at 0.3pu load torque? Probably not a lot.
So maybe if we zoom on a bit to get a better look:
Maybe not a lot there either so in we go again:
Which part of this do you not grasp?
SeeYour link is for special high torque motors, which is not what we were talking about. And I see nothing in it about voltage.
iwire,iwire,I expect a bit of more reflection on your part.
I added it to show that an induction motor can operate at 14% slip, for example.Your link is for special high torque motors, which is not what we were talking about. And I see nothing in it about voltage.
The foregoing discussion shows that the induction machine, when operating from mains
is essentially a constant speed machine. Many industrial drives, typically for fan or pump
applications, have typically constant speed requirements and hence the induction machine
is ideally suited for these.
My dear Besoeker,let me play with you more.The curves I provided are for an actual motor in operation on a centrifugal load.
You have once again demonstrated your total lack of experience in this field.My dear Besoeker,let me play with you more.
In your post #170,you naively marked the 0.3 p.u. load point on the straight,stable operating portion of the torque-speed characteristic of the motor.This would be correct,if the load is of the constant torque type.But,as you stated,the load is of variable torque type and its 0.3 p.u load point occurs on its curve (red line in your diagram) near the 0.75 p.u speed.Suppose your client asks you that he wants to operate his centrifugal load (per your statement)at 0.3 p.u load point.How are you going to do it? (Do not say by varying the frequency.It is not relevant to the present discussion.