Wrong on a number of technical issues but your greatest wrong is in trying to tell others, who clearly have much more expertise in this field than you, that you know better. You don't.
You can learn from listening to those of us who have been there and done that.
It's your choice whether you do.
I do listen.See your post#138 wherein you argued that slip of the motor changes too negligibly.But I stressed that with reduced voltage energy saving method,the speed (as well as water output in the case pump) changes appreciably.That i am right can be seen from the case study of Indian Bureau of Energy efficiency
ELECTRIC MOTORS
Bureau of Energy Efficiency,
(under Ministry of Power, Government of India)
Hall no.4, 2nd Floor, NBCC Tower,
Bhikaji Cama Place,
New Delhi ? 110066.
Indian Renewable Energy Development Agency,
Core 4A, East Court,
1st Floor, India Habitat Centre,
Lodhi Road,
New Delhi ? 110003
.
By
Devki Energy Consultancy Pvt. Ltd.,
405, Ivory Terrace, R.C. Dutt Road,
Vadodara ? 390007, India.
2006
Case Study-
Operation in STAR connection for under loaded motors
Industry / Sector Edible Oil manufacturing Plant
year of Implementation: 1995
Cost Benefit Analysis
_ Type of Measure: No cost measure
_ Annual energy Savings: 4560 kWh
_ Actual cost savings: Rs 18,240
_ Actual investment: Minor
_ Payback: Immediate
Principle
When motors are under-loaded, their torque requirement is less compared to that at
full load. Hence the impressed voltage required at the motor windings is less due to
less torque required.
'In Delta-Connection', the line voltage is impressed on each motor phase winding.
Whereas in ?star connection?, line voltage divided by _3 is impressed on each phase
winding.
When ?star? connected, the current drawn by the motor drops significantly, power
factor increase also takes place. Overall power saving is likely to be 10 to 20%
depending on the extent of under loading.
Background
In this edible oil (Vanaspati) manufacturing company, A 25 hp/18.5 KW motor was
driving a cooling water circulation pump. The electrical measurements in ?delta
connection? were as follows :
Voltage : 415 V
Current : 18.5 A
Power Factor : 0.505
Power Input : 6.72 KW
Speed : 1469 rpm
Considering the fact that the load was less than 30%, it was decided to operate the
motor in star connection.
Voltage : 415 V
Current : 9.5 A
Power Factor : 0.873
Power Input : 5.96KW
Speed : 1454 rpm
It may be noted that the current has dropped but the power Considering the fact that
the load was less than 30%, it was decided to operate the motor in star connection.
Note that the reduction in power from 6.72 kW to 5.96 kW is not only due to
reduction in motor losses, but also a due to reduction in speed of driven equipment.
---------
Do you also listen?