It's a bad unanswerable question. There is not enough information to answer.
There is no definite correct answer with what was given, still is somewhat reasonable to design for 40% fill like we do with power conductors, and if you go much over that is pretty likely to cause enough strain to potentially cause performance issues with the cables. You don't have to "break" conductors but can still reduce maximum data speed capabilities if you strain the cables.It's a bad unanswerable question. There is not enough information to answer.
I am not convinced that article 800 would apply to such circuits.Found it. Fill does not apply 800.110(B), so this is a bad question.
The answer to the question is 3/4. Question has cable size as .22 (inches) not sq inches, so you have to convert inches to sq inches then Table 4 Ch 9 under 40% column since there is more than 2 cables. Wow generated great conversation. Hope someone other than my self learn something out of this especially those studing for their test. READ the question and don't let wording trip you upI am not convinced that article 800 would apply to such circuits.
Read what 800.1 says.
Then read carefully how 800.2 defines a "communications circuit".
Very little actually falls under Article 800. The scope of that article ends at the first piece of customer owned equipment.I am not convinced that article 800 would apply to such circuits.
Read what 800.1 says.
Then read carefully how 800.2 defines a "communications circuit".
I am not convinced that article 800 would apply to such circuits.
Read what 800.1 says.
Then read carefully how 800.2 defines a "communications circuit".
Very little actually falls under Article 800. The scope of that article ends at the first piece of customer owned equipment.
Fill does not apply 800.110(B).
Yes, question doesnt state each cable is .22 inches, so i looked at Table 1 and said 1 inch, but didnt convert to sq inch before looking at chart, so 40% rule apply or not after converting to sq inch?
I am also confused on this. The article talks about abandoned cables etc. Why are you saying that it stops at the first piece of equipment other than the bonding diagram. @don_resqcapt19Very little actually falls under Article 800. The scope of that article ends at the first piece of customer owned equipment.
Here is a good article on this:
Consulting - Specifying Engineer | Clarifying NEC Articles 725 and 800
Consulting - Specifying Engineer - Learning objectives Understand NEC Articles 725 and 800, and how they affect network cabling for electrical engineers. Determine which Article to startwww.csemag.com
After reading the article, and considering the comments of some of y'all on here, I agree the intent is that 800 not apply and it falls under 725. I do still think they botched the wording in the definition of communication circuit and it is ambiguous going off that alone. Reading through 725, it is not immediately clear that that applies either, but the key is (this was noted in the CSE article) that 645.3(D) sends you to 725.
BUT......I still see 800 applying in some/many situations. It would depend on the equipment arrangement and ownership. For example If I run a cat 6 cables for POTS and/or DSL from the network interface box, it seems 800 would apply. Same could be said for cable/fiber modems. I have never had fiber/cable/dsl so I am unfamiliar with the specific equipment and ownership details.
It is if the telephone wiring is connected to a privately owned PBX....
So if we were going to get into semantics here, telephone wiring should be under 725. And as far as I'm concerned, data is just fine where it is under 800. Those "consulting engineers" really need to have a better understanding and not quote things as fact.
-Hal
That article is nothing but opinion by those who would mince words! Nothing in the NEC supports their conclusion.
For instance, we have computers supplied by network cabling. According to those jokers the cabling is covered under 725. Now, what happens if you plug an IP phone into the same jack? Does it magically change the cabling to Art. 800?
Don't data networks connect to the internet? If the NEC actually defined a “communication circuit” as that which extends a communication utility circuit to a customer’s terminal equipment, wouldn't that be covered?
Lastly, what's the difference between telecom and data cabling anyway? Art 725 covers cables carrying sufficient voltage and current such that they need to be installed to prevent a hazard to people and property. Does data cabling carry any appreciable voltage and current? No. (Not talking about POE here.) Do telephone and other communications cables in Art 800 carry any appreciable voltage and current? Actually yes, and anybody who has come in contact with a POTS telephone line can tell you that the 90VAC ringing voltage can knock you for a loop. Not to mention the 48VDC that's there open circuit. Some carrier equipment can have up to 200 volts supplied to it.
So if we were going to get into semantics here, telephone wiring should be under 725. And as far as I'm concerned, data is just fine where it is under 800. Those "consulting engineers" really need to have a better understanding and not quote things as fact.
-Hal
Electrical Classification of Data Circuits. Section 725.121(A)(4) shall apply to the electrical classification of listed information technology equipment signaling circuits. Section 725.139(D)(1) and 800.133(A)(1)(b) shall apply to the electrical classification of Class 2 and Class 3 circuits in the same cable with communications circuits.
I don't think I would classify that article as "opinion"...
Communications Circuit
: The circuit that extends voice, audio, video, data, interactive services, telegraph (except radio), outside wiring for fire alarm, and burglar alarm from the communications utility to the customer’s communications equipment up to and including terminal equipment such as a telephone, fax machine, or answering machine.
But normally does so through some transition equipment and you have two networks, your premises network and the off premises network. Go up one level and your internet provider has similar, their customer network and the rest of the world network which may involve multiple networks in a particular individual exchange of information path as well.They twist things around to make the definition of a Communications Circuit in 800 fit their opinion.
Just because the NEC uses "such as" and lists some of the common equipment of the time doesn't mean that the list is definitive like they insist with their own re-writing of the paragraph. That's a tired old argument we've heard every time this subject comes up. Read the quote above. That's NOT what it means.
The internet certainly extends data from outside wiring and computers are certainly terminal equipment.
-Hal