Raceways

Status
Not open for further replies.

sirhc

Member
Can a disconnect or combination of disconnects be used as a raceway. In other words, could I pass a piece of mc cable through five disconnect switches to feed a service receptacle mounted on the bottom of the fith disconnect? 404.3 (B)----312.8
 
Welcome to the forum,..I think the answer is yes. This image was taken from this article ,.. http://ecmweb.com/mag/electric_stumped_code_41/

707ecmCQfig1.jpg
 
Depends on 2 things:

~wires being passed through do not take up more than 40% of the space
~you strip the MC first!



~Matt
 
Last edited:
I have five disconnects on the outside of a building. I want to bring all my line side branch conductors in through the first disconnect, to the second, to the third, to the fourth and then to the fifth. I then want to route my load conductors back in the same race way. this is only an example and not a good practice in my opinion, but is a code violation??
 